The Chartership Forum

Structural Dynamics / Free vibration and damping

Measuring damping from a decay trace

The logarithmic decrement, derived and then used — and an honest account of why the number it gives is the least reliable input to any dynamic model.

Lesson review: expert verification remains open

This lesson has received a full-context editorial review and a check of its technical explanations. Selected arithmetic has been checked separately. This is not independent engineering sign-off.

Checks needed for project use

  • A dynamics reviewer must confirm excitation models, damping, modal assumptions and any comfort or serviceability interpretation. Small displacement alone is not an acceptance criterion.
  • Independent validation of the associated interactive implementation, input domain and project applicability remains required; this review checks lesson context and selected calculations, not design certification.
  • Review decay measurements for multimode beating, noise and amplitude dependence before assigning service damping.

These are educational models and exercises. Check their assumptions before using the results. The full technical content and every diagram have not yet been independently verified.

Concrete and steel calculations retain their stated first-generation Eurocode teaching basis. Use the standards and amendments specified for your project; do not mix generations without an appropriate design basis.

Read the lesson register and outstanding review notes

Why this matters

Mass can be calculated. Stiffness can be calculated. Damping cannot — it has to be measured, or taken from measurements on structures believed to be similar.

That single fact shapes a great deal of practice. It is why design damping values are tabulated by structural type rather than derived, why resonant response predictions carry wide uncertainty, and why a vibration serviceability assessment is often presented as a range rather than a number.

By the end of this lesson you should be able to

  • Derive the logarithmic decrement from the free-vibration solution
  • Convert a logarithmic decrement to a damping ratio, exactly and approximately
  • Explain why several cycles must be used rather than one
  • State what a decay test does and does not establish

From first principles

The logarithmic decrement

We want to show: Show that successive peaks of a damped free vibration fall by a constant RATIO, and use that to extract the damping ratio from a measured trace.

The decaying exponential envelope has a property that makes this measurement possible: over any fixed interval of time it falls by the same fraction, wherever you start. Successive peaks are separated by exactly one damped period, so the ratio between them is the same every cycle — and that single ratio contains the damping.

Try it

Estimating damping from a decay trace

This is the measurement an engineer actually makes on site. Choose two peaks and read the damping off them.

%
Displacement against Time. Measured decay reaches a peak magnitude of 40 mm.024681012-40-30-20-10010203040peak 0peak 1Time (s)Displacement (mm)
Displacement against Time. Measured decay reaches a peak magnitude of 40 mm.
PeakMeasured (mm)Ratio to previous
040.00—
133.571.1914
226.891.2487
323.081.1650
418.751.2310
515.411.2164
613.151.1719
710.501.2531
Cycles between the peaks, n
1
Amplitude ratio
1.1914
δ = (1/n) ln(ratio)
0.175
ζ = δ/√(4π² + δ²)
0.0279
ζ ≈ δ/2π (approximation)
0.0279
True value
0.0300
Error in the estimate
-7.1%

Over one cycle the amplitude falls by only 17.2%. With a 2% reading error on each peak, that is why the estimate is 7% out. Increase the separation between the peaks.

What this measurement cannot tell you

  • It measures the damping at the amplitude of the test. Real damping is amplitude-dependent, and a small-amplitude test on a building will report less damping than the same building shows in a storm.
  • It assumes viscous damping. Friction in cladding, joints and finishes is not viscous, and fitting an exponential to it gives a number that works only over the range measured.
  • The very late peaks are the least reliable, because the signal has fallen towards the noise floor of the instrument.

What this shows: The logarithmic decrement works because consecutive peaks fall by a constant RATIO. Using peaks many cycles apart is not a refinement — at realistic damping levels it is the difference between a usable estimate and noise.

Try it

Where the energy goes

Release the mass from rest and watch the amplitude fall — then watch the energy account that explains why.

s
Displacement against Time. Displacement reaches a peak magnitude of 40 mm. Envelope reaches a peak magnitude of 40.1 mm. reaches a peak magnitude of 40.1 mm.0123456789-40-30-20-10010203040Time (s)Displacement (mm)
  • Displacement
  • Envelope
Displacement against Time. Displacement reaches a peak magnitude of 40 mm. Envelope reaches a peak magnitude of 40.1 mm. reaches a peak magnitude of 40.1 mm.
t = 0.00 s
Energy against Time. Kinetic reaches a peak magnitude of 424 J. Strain reaches a peak magnitude of 493 J. Dissipated (cumulative) reaches a peak magnitude of 493 J. Total mechanical reaches a peak magnitude of 493 J.01234567890100200300400500Time (s)Energy (J)
  • Kinetic
  • Strain
  • Dissipated (cumulative)
  • Total mechanical
Energy against Time. Kinetic reaches a peak magnitude of 424 J. Strain reaches a peak magnitude of 493 J. Dissipated (cumulative) reaches a peak magnitude of 493 J. Total mechanical reaches a peak magnitude of 493 J.
Show the numbers behind this plot
Initial energy E₀
493 J
Energy remaining now
100.0%
Amplitude remaining now
100.0%
Logarithmic decrement δ
0.315
Cycles to half amplitude
2.2
Cycles to 1% amplitude
14.6

Energy goes as amplitude squared, so when the amplitude has halved, three quarters of the energy has already gone. That is why a structure that still looks like it is moving may have almost nothing left in it — and why a damping estimate taken from the tail of a decay trace is the least reliable part of the record.

What this shows: Amplitude decays because the damper is converting mechanical energy into heat. Energy falls as the SQUARE of amplitude, so the energy is gone long before the motion looks small.

Worked example

Reading damping off a measured trace

Given

  • A decay record from a floor after a heel-drop test
  • First peak: 0.412 mm
  • Sixth peak: 0.198 mm
  • Measured frequency 5.8 Hz

Find

The damping ratio, and what can and cannot be concluded from it.

Assumptions

  • Peaks are read one damped period apart, so five cycles separate them
  • The response is dominated by a single mode

    Practice

    The first peak of a decay trace is 12.0 mm and the fifth is 5.4 mm. What is the logarithmic decrement?

    Practice

    For that trace, what is the damping ratio as a percentage?

    Practice

    A structure has 2% damping. Over how many cycles must peaks be separated for the amplitude ratio to reach 2.0?

    Check yourself

    A decay trace shows peaks falling by a constant AMOUNT each cycle — 10 mm, 8 mm, 6 mm, 4 mm — rather than by a constant ratio. What does this indicate?

    Check yourself

    Two otherwise identical structures are released at the same initial amplitude and compared against the same detection threshold. One shows12cycles and the other3. What differs in the constant-viscous model?

    Worked example

    Damping from a decay trace, five cycles apart

    Given

    • A heel-drop test on a composite floor
    • The first measured peak is 12.0 mm
    • The peak five cycles later is 7.4 mm

    Find

    The damping ratio

      Worked example

      How long does it take to stop?

      Given

      • The same floor, measured at ζ = 1.54 %
      • A second floor after fit-out, at ζ = 5 %

      Find

      The cycles needed for the amplitude to fall to a tenth, and to a half

        Summary

        • δ = (1/n)ln(xᵢ/xᵢ₊ₙ) — the log of the amplitude ratio, per cycle
        • ζ = δ/√(4π² + δ²) exactly, and ζ ≈ δ/2π below about 20% damping
        • The measurement needs no knowledge of mass or stiffness, which is what makes it practical
        • Use enough cycles for the amplitude ratio to exceed 2 — about six at 2% damping
        • A constant amplitude RATIO confirms viscous damping; a constant difference denies it
        • A decay test measures damping at the amplitude tested, in the mode excited, in the condition tested
        • Service damping is usually higher than a bare-structure test reports