Relationships, overhangs and contraflexure

The calculus behind the shapes, and what happens when a beam hangs over its support.

Lesson review: expert verification remains open

This lesson has received a full-context editorial review and a check of its technical explanations. Selected arithmetic has been checked separately. This is not independent engineering sign-off.

Checks needed for project use

  • An independent structural reviewer must check remaining derivations, diagrams, sign conventions and the interactive models across their full input ranges.
  • Model applicability, diagrams and implementation across all input cases remain subject to independent engineering review.

These are educational models and exercises. Check their assumptions before using the results. The full technical content and every diagram have not yet been independently verified.

Concrete and steel calculations retain their stated first-generation Eurocode teaching basis. Use the standards and amendments specified for your project; do not mix generations without an appropriate design basis.

Read the lesson register and outstanding review notes

Why this matters

Once you see that these three diagrams are linked by slopes and areas, you stop memorising shapes and start deducing them. It also gives you a fast way to check anyone's diagram, including your own.

By the end of this lesson you should be able to

  • State how load, shear and moment relate to each other
  • Use areas under the shear diagram to get moments
  • Handle overhangs and find points of contraflexure
Load, shear and moment
dVdx=−wdMdx=V\frac{dV}{dx} = -w \qquad \frac{dM}{dx} = V

What it calculates: How the three diagrams are connected: the slope of the shear diagram is the load intensity, and the slope of the moment diagram is the shear.

w
Downward distributed load intensity (kN/m)
V
Shear force at the section (kN)
M
Bending moment at the section (kN·m)
x
Distance along the beam (m)

This assumes

  • The beam is straight
  • Loads act perpendicular to the beam
  • No applied point moments at the section considered

In plain terms: Read it backwards and it becomes practical: the change in shear between two points is the load in between, and the change in moment is the area under the shear diagram between them. That is usually quicker than starting again from the reactions.

Predict first

The shear force at a section is zero. What does that tell you about the bending moment there?

An overhang is a length of beam projecting past its support. The overhang hogs, because the load out there tries to lift the beam off the far support and bends the beam the other way. Somewhere between the sagging span and the hogging overhang the moment must pass through zero. That point is called a point of contraflexure.

A ten metre beam supported at zero and seven metres with a three metre overhang, carrying a uniform load, showing sagging in the span and hogging over the support.4 kN/m11.43 kN28.57 kNShear force V (kN)-16.57Bending moment M (kN·m)-18.00
The moment is sagging in the main span, crosses zero, then hogs over the support and through the overhang.

Practice

A simply supported beam spans 10.0 m and carries a UDL of 8 kN/m over its whole length. What is the maximum bending moment?

Practice

A cantilever 5.0 m long carries a UDL of 4 kN/m. What is the magnitude of the maximum bending moment?

Practice

A simply supported beam spans 12.0 m under a UDL of 6 kN/m. What is the maximum bending moment?

Practice

On a beam, the signed area under the shear-force diagram between two points, read from left to right, is +45 kN·m. If the bending moment at the first point is 20 kN·m, what is it at the second?

Summary

  • dV/dx = −w and dM/dx = V
  • Change in moment between two points = area under the shear diagram
  • Under the downward loading shown, the overhang hogs and part of the main span sags; other load arrangements can change those regions
  • Contraflexure is where the moment changes sign and the tension face swaps