The Chartership Forum

Structural Steel Design / Bolts, pins and welds

Preloaded bolts, welds, and what detailing protects

Preloaded connections transfer load by friction before slip. Fillet welds are assessed on their effective throat, and connection resistance depends on the bolt and weld arrangement.

Lesson review: expert verification remains open

This lesson has received a full-context editorial review and a check of its technical explanations. Selected arithmetic has been checked separately. This is not independent engineering sign-off.

Checks needed for project use

  • A steel-design reviewer must check the first-generation calculation profiles, second-order analysis assumptions, connection rules and execution references against the applicable standards and amendments.
  • Slip, bearing-type shear and ultimate resistance are separate checks. Weld directional method must also satisfy its normal-stress condition and effective-length/detailing requirements. Full-strength rule of thumb is not complete joint verification.

These are educational models and exercises. Check their assumptions before using the results. The full technical content and every diagram have not yet been independently verified.

Concrete and steel calculations retain their stated first-generation Eurocode teaching basis. Use the standards and amendments specified for your project; do not mix generations without an appropriate design basis.

Read the lesson register and outstanding review notes

Why this matters

Three connection details need careful interpretation. Slip resistance and bearing-type ultimate resistance describe different limit states. An equal-leg 6 mm fillet has a throat of approximately 4.2 mm. And the spacing rules that look like drawing-office convention are inputs to the bearing resistance calculated in the last lesson.

By the end of this lesson you should be able to

  • Explain what a preloaded bolt does and why it is specified
  • Say why applied tension reduces slip resistance
  • Size a fillet weld on its throat and know when transverse loading helps
  • Say what each detailing rule protects

What you should already know

  • Bolt shear and bearing (previous lesson)
  • The von Mises criterion (Module 1)
  • Ultimate strength and why connections work to fu (Module 1)

Slip resistance of a preloaded connection

Tighten a bolt hard enough and it clamps the plies together. The load then passes across the interface by friction, not by the bolt bearing on the side of its hole. The slip-resistance calculation depends on preload, friction, interfaces and the applicable factors. Bolt shear, bearing, tension and interaction checks may still be required for the connection category and design situation.

That leads somewhere counter-intuitive. For an M20 grade 10.9:

Preload Fp,C = 0.7 fub As172 kN
Slip resistance, one surface68.6 kN
The same bolt in bearing-type shear98.0 kN

These figures compare different limit states. The lower slip resistance does not establish that the connection has a lower ultimate resistance.

Preloading is used where slip needs to be controlled at the specified serviceability or ultimate limit state. A bearing-type connection has clearance holes, so it moves a millimetre or two before the bolts bear. That movement is harmless in most structures and unacceptable in some: where fatigue matters, where a joint must not lose its alignment, where a connection is part of a stiffness-critical bracing system, or where reversal would work a bolt back and forth in its hole.

And one interaction catches people out. Applied tension relieves the clamping force, so it reduces the slip resistance:

Applied tensionSlip resistanceLost
068.6 kN—
40 kN55.8 kN19%
80 kN43.0 kN37%

A bolt group carrying both shear and tension therefore loses slip capacity exactly when it is busiest.

Try it

What preloading actually buys

A preloaded bolt clamps the plies and friction carries the load. Compare that with the same bolt in a bearing-type connection, and watch what applied tension does to it.

20 mm

Bolt grade

1
0.50
0 kN
Slip resistance against the same bolt in bearing-type shearslip resistance68.6 kNsame bolt, bearing98.0 kNpreload 172 kN · slip factor 0.5lost to applied tension 0%
Preload Fp,C
172 kN
Slip factor μ
0.50
Friction surfaces
1
Slip resistance Fs,Rd
68.6 kN
Same bolt in bearing
98.0 kN
Slip over bearing
0.70 ×
Applied tension
0 kN
Lost to that tension
0 %

Preload 172 kN and slip resistance 68.6 kN across 1 surface, using slip factor 0.5. The separate threaded-plane bolt shear resistance is 98.0 kN; plate bearing and the other checks required for the connection category still apply.

Things worth trying

  • Start at M20 grade 10.9, one surface, μ = 0.5, no tension. The slip resistance is 68.6 kN against 117.6 kN for the same bolt in bearing — a preloaded connection is WEAKER, and it is specified anyway.
  • That is the point of it. Bearing-type connections have clearance holes and move a millimetre or two before the bolts bear. Preloading buys the absence of that movement, not strength.
  • Add a second friction surface. The slip resistance doubles, because friction acts on each interface independently.
  • Take the slip factor from 0.5 down to 0.2 — a painted rather than a blasted surface. The resistance falls in proportion. Surface preparation is a structural specification here, not a finish.
  • Now add applied tension. At 80 kN the slip resistance has fallen 37%, because the tension is relieving the clamping force the friction depends on.
  • Keep adding tension until the resistance reaches zero. A bolt group carrying both shear and tension loses slip capacity exactly when it is busiest.
  • Switch to grade 8.8 and watch both bars fall together — the preload and the shear resistance both go with fub, so the comparison between them barely moves.

A fillet weld is smaller than it looks

A fillet weld's strength is taken on its throat — the shortest distance through the weld — not on its leg. For an equal-leg fillet the throat is s/√2:

LegThroat
4 mm2.83 mm
6 mm4.24 mm
8 mm5.66 mm
10 mm7.07 mm

So a 6 mm fillet is structurally a 4.2 mm weld. That is not a deduction or an allowance — it is where the failure plane is.

Two methods, and the difference is real.

The simplified method takes the resultant force on the throat, whatever direction it acts in, against a single design shear strength. Its applicability and conservatism depend on satisfying the method’s assumptions and the other required weld checks.

The directional method resolves the force into components on the throat and applies the von Mises criterion. It gives more, and how much more depends on the angle:

Angle to the weld axisGain
0° (along the weld)1.000
30°1.044
45°1.095
60°1.155
90° (across the weld)1.225

For the stated idealised loading and throat geometry, the directional expression permits up to about 22.5% more resistance, subject also to its normal-stress limit and other weld rules. The factor is derivable, not fitted: resolving a force at θ onto the 45° throat and applying von Mises gives a resistance proportional to 1/√(3 − sin²θ), which is exactly √3 : √2 between the two extremes.

Try it

Throat, direction, and the full-strength leg

A double-sided fillet joining a plate to a support. Compare the two design methods, then find the leg at which the weld stops being the weak link.

6 mm
90 degrees
250 mm
12 mm
Weld capacity by both methods, against the plate it joinssimplified method533 kNdirectional method653 kNthe plate itself1065 kNleg 6 mm gives a 4.24 mm throat · directional gain 22.5%
Weld leg s
6 mm
Throat a
4.24 mm
Design shear strength fvw,d
251 N/mm²
Simplified method
1067 N/mm
Directional method
1307 N/mm
Directional gain
22.5 %
Capacity, simplified
533 kN
Capacity, directional
653 kN
The plate's own capacity
1065 kN
Full-strength leg needed
12.0 mm
As a fraction of the plate
1.00 × t
Weld metal, relative to 6 mm
1.00 ×

The weld is the weak link: 653 kN against the plate's 1065 kN. A 12.0 mm leg would make it full strength, at 4.0 times the weld metal.

Things worth trying

  • Start at a 6 mm leg. The throat is 4.24 mm — a fillet weld is always smaller structurally than it looks, because strength is taken on the shortest path through it.
  • Take the angle from 90° down to 0°. The directional method's advantage disappears entirely: 22.5% across the weld, nothing along it.
  • At 90° with a 250 mm run each side, the two methods give 654 and 534 kN. If the applied load were 600 kN they would disagree about whether it passes — that is not a rounding difference.
  • Set the plate to 12 mm and raise the leg until the weld bar passes the plate bar. It happens at about 12 mm — for S355, a double fillet with leg equal to the plate thickness is roughly full strength.
  • Change the plate to 20 mm and repeat. The full-strength leg moves with it, still at about 1.0 × t. The neatness is a coincidence of the S355 numbers, not a law.
  • Watch the weld-metal figure as you raise the leg. Volume goes with the square, so a 12 mm fillet costs four times a 6 mm one — strength doubles, cost quadruples.
  • Try a very short run with a large leg against a long run with a small one, at the same weld metal. Length is usually the cheaper way to buy capacity.

Worked example

A bracket welded to a column flange

Given

  • A 12 mm S355 plate welded to a column flange with a double-sided fillet
  • Parent metal fu = 490 N/mm², βw = 0.9, γM2 = 1.25
  • The connection carries 600 kN acting across the weld run
  • Weld run length 250 mm each side

Find

The leg size needed, and whether a full-strength weld would be sensible instead.

Assumptions

  • βw and γM2 are calibrated and unverified here
  • The weld is treated as loaded uniformly along its length; a real bracket also has a moment, which Module 13 covers

    Detailing rules protect calculations you have already done

    The minimum spacings are not drawing-office convention. Each one is protecting a number.

    RuleTypical minimumWhat it protects
    End distance e₁1.2 d₀Below this the bolt tears out through the end of the plate, and the bearing calculation does not apply at all
    Edge distance e₂1.2 d₀The k₁ coefficient in the bearing resistance, and splitting of the plate sideways
    Pitch p₁2.2 d₀Bolts too close share one failure surface and the group tears out as a block
    Gauge p₂2.4 d₀The same across the load — plus it has to be physically possible to get a spanner in
    Maximum pitchthe lesser of 14t and 200 mmThe plies separating between fasteners: water gets in, and the plate can buckle locally

    Notice that the first four are all measured against the hole, not the bolt. That is why going up a bolt size without opening the pattern out tightens every one of them at once — the effect the predict block in the last lesson turns on.

    The minima are what make the bearing calculation valid. They are an input to a resistance, not a separate tidiness requirement.

    Practice

    What is the throat thickness of an 8 mm equal-leg fillet weld, in mm?

    Practice

    A weld metal has fu = 490 N/mm², βw = 0.9 and γM2 = 1.25. What is fvw,d in N/mm²?

    Practice

    By what factor is a transversely loaded fillet weld stronger than a longitudinally loaded one, by the directional method?

    Practice

    A preloaded M20 grade 10.9 bolt has As = 245 mm². What is its preload Fp,C, in kN? Take Fp,C = 0.7 fub As.

    Check yourself

    Why is a preloaded bolted connection specified, given that its slip resistance is usually LOWER than the same bolts in bearing?

    Summary

    • Before slip, friction transfers the shear; check the additional bolt and plate resistances required for the connection category
    • M20 10.9: 172 kN preload, 68.6 kN slip resistance and 98.0 kN threaded-plane shear resistance
    • Preloading controls slip at the specified limit state; the required ultimate connection checks still apply.
    • Applied tension relieves the clamp: 80 kN of tension cost 37% of the slip resistance
    • A fillet weld's strength is on its THROAT — a 6 mm leg is a 4.24 mm weld
    • The directional method beats the simplified one by up to 22.5%, and it is derivable
    • For S355 a double fillet with leg ≈ plate thickness is full strength — a coincidence, not a law
    • Every minimum spacing is measured against the HOLE, and protects a resistance you have calculated