The Chartership Forum

Soil Mechanics / Consolidation and settlement with time

How much: the e–log σ′ idealisation

Compression and recompression indices, preconsolidation stress, and the primary settlement equation.

Lesson review: expert verification remains open

This lesson has received a full-context editorial review and a check of its technical explanations. Selected arithmetic has been checked separately. This is not independent engineering sign-off.

Corrections checked in this pass

  • Replaced the discontinuous consolidation approximation with the uniform-initial-pressure series and a consistent inverse.

Checks needed for project use

  • A geotechnical reviewer must check laboratory interpretation, classification conventions and the limits of drained, undrained and one-dimensional idealisations.
  • Initial excess-pressure distribution, variation in cv, drainage and secondary compression require assessment.

These are educational models and exercises. Check their assumptions before using the results. The full technical content and every diagram have not yet been independently verified.

Concrete and steel calculations retain their stated first-generation Eurocode teaching basis. Use the standards and amendments specified for your project; do not mix generations without an appropriate design basis.

Read the lesson register and outstanding review notes

Why this matters

To predict how much a clay will settle we need its stress–compression behaviour. Plotted as void ratio against the logarithm of effective stress, that behaviour straightens into lines whose slopes — CcC_c and CrC_r — are all we need. The soil's stress history, marked by the preconsolidation stress, decides which slope applies.

Load a clay in the laboratory (the oedometer test, Module 12) and plot void ratio ee against log⁡10σ′\log_{10}\sigma'. Two features appear:

  • A steep, straight virgin compression line — the path a clay follows when it is loaded beyond any stress it has felt before. Its slope is the compression index CcC_c.
  • A much flatter recompression/swelling line — the path followed on unloading and reloading within the past maximum stress. Its slope is the recompression index CrC_r (with Cr≪CcC_r \ll C_c, typically Cr≈0.1C_r \approx 0.1–0.2 Cc0.2\,C_c).

The stress at the corner between them — the largest effective stress the soil has ever carried — is the preconsolidation stress σc′\sigma'_c.

Compression index
Cc=−ΔeΔ(log⁡10σ′)C_c = -\dfrac{\Delta e}{\Delta(\log_{10}\sigma')}

What it calculates: the slope of the virgin compression line on the e–log σ′ plot

Cc
compression index (dimensionless)
Δe\Delta e
change in void ratio over one part of the line
σ′\sigma'
vertical effective stress (kPa)

In plain terms: A larger Cc means a more compressible clay. Soft, high-plasticity clays have the largest Cc and settle the most.

A clay is normally consolidated (NC) if its present effective stress equals the largest it has ever carried (σ0′=σc′\sigma'_0 = \sigma'_c, so the overconsolidation ratio OCR=σc′/σ0′=1\text{OCR} = \sigma'_c/\sigma'_0 = 1). It is overconsolidated (OC) if it has been more heavily loaded in the past — by ground since eroded, ice long melted, or a water table that has since risen — so σc′>σ0′\sigma'_c > \sigma'_0 and OCR>1\text{OCR} > 1.

This matters enormously. An OC clay loaded within its past maximum follows the flat recompression line and settles little; push it past σc′\sigma'_c and it drops onto the steep virgin line and settles far more. Predicting settlement therefore begins with finding σc′\sigma'_c.

From first principles

Primary consolidation settlement from the compression index

We want to show: Turn the slope of the e–log σ′ line into the settlement of a clay layer of thickness H.

The layer shortens because its voids shrink. The e–log σ′ line tells us how much the void ratio drops for a given stress increase; converting that void-ratio drop into a thickness change, over the layer, gives the settlement.

Try it

Consolidation settlement and time

How much a clay layer settles, and how that settlement unfolds. Stress history and drainage both matter.

4.0 m
0.40
80 kPa
120 kPa
100 kPa
2.0 m²/yr

Drainage

3.0 yr

Fixed for clarity

  • Initial void ratio e₀ = 0.9; recompression index Cr = 0.15·Cc.
  • OCR = σ'c/σ'₀; loading past σ'c drops the clay onto the steep virgin line.
  • Drainage path Hdr = H/2 (double) or H (single); time scales with Hdr².
0171mm3 yrtime (years)final s∞t₉₀
OCR = σ'c/σ'₀
1.50
Final primary settlement s∞
171 mm
At t — degree U
98 %
At t — settlement
167 mm
Time to 50% t₅₀
0.4 yr
Time to 90% t₉₀
1.7 yr

The load pushes past σ'c: a small recompression part plus a large virgin part — most of the settlement is virgin compression.

Worked example

Settlement of an overconsolidated clay that crosses σ′c

Given

  • Clay layer 4 m thick, e₀ = 0.9
  • Cc = 0.40, Cr = 0.06
  • In-situ vertical effective stress σ′0 = 80 kPa
  • Preconsolidation stress σ′c = 120 kPa (OCR = 1.5)
  • A wide fill raises the stress by Δσ′ = 100 kPa, so σ′f = 180 kPa

Find

The primary consolidation settlement.

Assumptions

  • One-dimensional compression under the wide fill; drained final state so Δσ′ = Δσ.

    Practice

    A normally consolidated clay layer is 3 m thick with e₀ = 0.8 and Cc = 0.3. A wide load raises the vertical effective stress from 100 kPa to 200 kPa. What is the primary consolidation settlement, in mm?

    Summary

    • On an e–log σ′ plot, clay follows a steep virgin line (slope Cc) and a flat recompression line (slope Cr).
    • The preconsolidation stress σ′c is the largest effective stress the soil has ever carried; OCR = σ′c/σ′0.
    • Primary settlement s = Cc·H/(1+e₀)·log₁₀(σ′f/σ′0), using Cr below σ′c and splitting at σ′c if the load crosses it.
    • An overconsolidated clay settles little until the load pushes it past σ′c.